Date: May 19, 1987 08:54
From: KIM::FRYE
To: @SYS$MAIL:EVERYBODY
THIS MESSAGE IS DIRECTED TO ALL PERSONNEL HAVING ACCESS TO OUR MAIN COMPUTER ROOM. Having recently completed installation of a second a/c backup system for the computer room, I would like to take this time to define it's operation. Should the main a/c unit for the comp- uter room fail, a red lite located in the center of the room on the hallway wall will come on. Please follow the instructions posted. A test was conducted following the compleation of this system. The results showed that all the computer equipment could remain running as the room temp erature remained normal. The additional backup air was supplied from a/c #2 and no complaints were received from that area during the four hour test. Bob