COMPUTER ROOM A/C

(1 / 1)


THIS MESSAGE IS DIRECTED TO ALL PERSONNEL
HAVING ACCESS TO OUR MAIN COMPUTER ROOM.

Having recently completed installation
of a second a/c backup system for the
computer room, I would like to take this
time to define it's operation.

Should the main a/c unit for the comp-
uter room fail, a red lite located in
the center of the room on the hallway
wall will come on. Please follow the
instructions posted.

A test was conducted following the 
compleation of this system.  The results
showed that all the computer equipment
could remain running as the room temp
erature remained normal.  The additional
backup air was supplied from a/c #2 and
no complaints were received from that
area during the four hour test.

Bob
Message 1 of 1

May 19, 1987